#1

Question:
Why does MAG 8000 show negative flow?
Answer:

Flow can be in another direction than expected
Flowmeter is mounted in wrong direction. The flowmeter must be mounted according to the arrow shown on the sensor

Solution if the flowmeter is wrongly mounted:


Mount the flowmeter in the opposite direction

Change parameter ID327 from “1” to “-1” using PDM and mark the sensor accordingly (e.g. by removing/turning the arrow label indicating the flow direction).